For AI agents: the complete documentation index is available at https://docs.ovhcloud.com/es/llms.txt, the full documentation bundle is available at https://docs.ovhcloud.com/es/llms-full.txt, and this page is available as Markdown at https://docs.ovhcloud.com/es/guides/network/load-balancer/create-probes.md.
Ir al contenido

Configuration of probes on an OVHcloud Load Balancer service

Ver como Markdown

Discover the general principles and use cases for probes

Objective

The OVHcloud Load Balancer allows you to distribute incoming traffic on a frontend to a set of servers in a destination farm.

It may happen that one of the servers in your farm is no longer available for various reasons, such as overload, an incident, or scheduled maintenance. When it encounters a connection error, your OVHcloud Load Balancer attempts to switch traffic to another server. The connection will be slowed down, but it will continue to function.

However, the causes of some unavailability are more subtle. For example, if a new version of the code is being deployed, the application may temporarily be in a transitional state and return 500 errors. In this specific case, one solution would be to mark the affected servers as unavailable in the API before the start of the maintenance, apply the configuration and update, and then mark the server as available again. This method is not ideal, but it works.

For more details on deploying a Blue-Green architecture with your OVHcloud Load Balancer, refer to this guide.

Probes are health checks. They periodically query each of your servers to ensure they are operational. If an error is detected, the server is automatically disabled until the situation is resolved.

This guide will present the general principles, as well as usage scenarios for probes, drawn from real-world use cases.

Requirements

  • Have an OVHcloud Load Balancer offer in your OVHcloud account. The service must be properly configured, with farms and servers set up.
  • Be logged in to your .

Instructions

Table of contents

Probe API overview

The probe API of your OVHcloud Load Balancer has been designed to be flexible and scalable.

Probes are configured directly on the farms. All servers in the same farm thus apply exactly the same probe. However, enabling or disabling a probe is specific to each server. It is therefore possible to "monitor" only certain servers in the same farm.

The list of available probes and their parameters can be consulted with the API call :

For more information on this call, we invite you to consult the Available probes section at the bottom of this guide.

The probes returned by this list can be configured on http and tcp farms via the following calls :

For more information on these calls, you can refer to the Probe handling section of this guide.

Examples

Check if the server accepts TCP connections

This is the simplest probe to set up. It is compatible with tcp and http farms. If no other probe is configured, you can activate this one to start. It works by periodically trying to open a connection on each of your servers. If the connection fails twice in a row, the server is put aside until it responds again.

In practice, this gives a probe :

FieldValue and description
serviceNameIdentifier of your OVHcloud Load Balancer
farmIdIdentifier of your TCP or HTTP farm
probe.type"tcp"

All other probe fields can remain at their default values. You just need to apply the configuration in the relevant area.

Test a specific HTTP page

By default, the HTTP probe sends an OPTIONS request on / in HTTP/1.0, without a domain name. This is sufficient in many cases, but some servers do not handle this method.
It is possible to perform much more powerful tests with the HTTP probe. For example, a good practice when exposing an HTTP service is to add a dedicated route for probes. It is common to find /status, /health, /check which return a summary of the service's status.

In practice, if you want to configure the probe to send a GET request to http://api.example.com/status, this gives :

FieldValue and description
serviceNameIdentifier of your OVHcloud Load Balancer
farmIdIdentifier of your TCP or HTTP farm
probe.typehttp
probe.methodGET
probe.urlhttp://api.example.com/status
probe.matchstatus
probe.pattern200 (several status codes can be added, separated by commas)

All other probe fields can remain at their default values. It is then sufficient to apply the configuration in the relevant area.

Use an external HTTP test

What if your service is, for example, an IMAP server that relies on an LDAP server for authentication ?
It is possible that the server accepts connections, but has a temporary connection issue with the LDAP server. If this happens, clients who are directed to this server could connect but not authenticate. The server should therefore be removed from the farm.

If a tcp type probe is used, it will be able to connect and consider the service available even though it is not the case.

In this scenario, the ideal would be for the health check to confirm that the base service is working. It is possible to indicate a specific port to use in the tests. This allows arbitrary tests to be set up for a service and exposed in HTTP, on a dedicated port.

For example, in this scenario, it would be possible to have an HTTP server on port 8080 that tests the IMAP server via the url /service/imap/status and returns OK when everything is fine. This would give in practice :

FieldValue and description
serviceNameIdentifier of your OVHcloud Load Balancer
farmIdIdentifier of your TCP or HTTP farm
probe.typehttp
probe.port8080
probe.methodGET
probe.url/service/imap/status
probe.matchcontains
probe.patternOK

It is then sufficient to apply the configuration in the relevant area.

Warning

If the HTTP service dedicated to monitoring your IMAP service itself fails, the IMAP service will also be considered as failed, even if it is in perfect working condition.

Reference

Probe handling

Configure a probe

Probes can be configured on a new farm (POST) or an existing farm (PUT). The two methods being equivalent, only the second one (PUT) will be presented here.

Parameters :

serviceName

The identifier of your OVHcloud Load Balancer.

farmId

The numeric identifier of your farm.

probe

type

The type of probe to enable. The probe types handled are :

tcp for a basic TCP connection test ;

http for an HTTP connection test. It is possible to specify the URL and method ;

smtp for a basic SMTP connection test ;

mysql for a basic MySQL connection test ;

pgslq for a basic PostgreSQL connection test ;

oco for a general status validation returned on port 79.

interval

The interval in seconds between two probe attempts. It must be at least 30 seconds.

port

The port that the probe should use, if it is different from the one configured on the farm. This allows you to delegate the server status validation to a third-party service on the machine and perform arbitrary probes.

method

The HTTP method to use if the probe is of type "http". The compatible methods are GET, HEAD and OPTIONS (default).

url

The URL to use for the tests, if the probe is of type "http". Its form must be [[https?://]www.example.com]/path/to/check. If a domain is specified, the request will be sent in HTTP/1.1 instead of HTTP/1.0 by default.

match

The type of comparator to use to check that the server is healthy. The comparators handled are default, status, contains and matches. The comparators are compatible with "http" and "tcp" probes.

pattern

The value to use as an argument for the comparator if it is different from "default".

forceSsl

Defines whether the probe should work in SSL/TLS even if the farm is configured to connect in classic TCP. This can be useful, for example, when your OVHcloud Load Balancer is configured to forward HTTPS traffic in TCP without decrypting it.

Other parameters can be edited via this call. As this guide focuses on probes, they are not documented here.

If a port other than the base port of the farm is configured on the probe, the proxyprotocol and ssl parameters are reset. Take the example of a farm configured to use proxyprotocol on port 4242 and a probe associated with port 8080: the latter will not send the proxyprotocol header when connecting to port 8080. The same applies to ssl, which can nevertheless be forced.

Warning

When a probe is configured on a farm, it must also be enabled on the servers.

Enable probes on a server

For a probe to be active, it must have been configured on the farm and enabled on the relevant servers. This call allows you to enable the probe :

Parameters :

serviceName

The identifier of your OVHcloud Load Balancer.

farmId

The numeric identifier of your farm.

serverId

The numeric identifier of your server.

probe

Indicates whether probe should be taken into account or not.

Other parameters can be edited via this call. As this guide focuses on probes, they are not documented here.

Available comparators

Four comparators are available to validate the result of a probe :

ComparatorDescription
defaultRuns a basic test, without parameters.
statusComma-separated list of valid HTTP return codes.
containsChecks that the pattern is in the response.
matchesChecks that the response matches the pattern regular expression.

The contains and matches comparators look for a match in the first 16 KB of the response. If it is longer, the part beyond will be ignored during the search. Note that for better performance, we recommend returning as little information as possible in your probes.

Available probes

The list of available probes can be obtained with the API call :

Response :

type

The type of probe to configure in the probe.type field of the farms.

The probe types handled are :

tcp for a basic TCP connection test ;

http for an HTTP connection test. It is possible to specify the URL and method ;

smtp for a basic SMTP connection test ;

mysql for a basic MySQL connection test ;

pgslq for a basic PostgreSQL connection test ;

oco for a general status validation returned on port 79.

port

Indicates whether the port can be configured for this probe.

method

The list of HTTP methods handled or null if none exist.

url

Indicates whether the probe URL can be configured.

matches

The list of available comparators for this probe. The interpretation of the probe.pattern field depends on this field. The potentially handled comparators are :

default the simplest test, without specific conditions. probe.pattern must be empty ;

status checks that the HTTP status code is in the comma-separated list ;

contains checks that the server response contains probe.pattern ;

matches checks that the server response matches probe.pattern.

TCP

This probe attempts to establish a TCP connection with the server. If the latter sends a "banner", it is possible to check that it matches a pattern. The default test simply ensures that the connection can be established.

FieldsDescription
typetcp
portConfigurable
methodNot supported
URLNot supported
matchesdefault, contains or matches
HTTP

This probe attempts to establish an HTTP connection with the server. If the latter responds, it is possible to check its HTTP status code or that the response body matches a pattern. The default test sends an OPTIONS request to the '/' page in HTTP/1.0, without the Host field.

FieldsDescription
typehttp
portConfigurable
methodGET, HEAD or OPTIONS
URLURL of the form [[https?://]www.example.com]/path/to/check
matchesdefault, contains or matches

If a URL is specified, the domain name and protocol are operational. If a domain name is specified, the "Host" field of the request will be filled in and the request will be sent in HTTP/1.1. If the protocol is specified, it must be consistent with the SSL configuration of the farm.

Info

It is recommended to configure at least the method with GET. Indeed, some servers -including Nginx- do not handle the OPTIONS method without prior configuration.

SMTP

This probe attempts to establish an SMTP connection with the server and sends the HELLO localhost command. If the latter responds, the probe checks that the return code starts with a "2" (success). This probe has no specific configuration options.

FieldsDescription
typesmtp
portConfigurable
methodNot supported
URLNot supported
matchesdefault
MySQL

This probe attempts to establish a MySQL connection with the server and analyses the server's response. This probe has no specific configuration options.

FieldsDescription
typemysql
portConfigurable
methodNot supported
URLNot supported
matchesdefault
PostgreSQL

This probe attempts to establish a PostgreSQL connection with the server and analyses the server's response. This probe has no specific configuration options.

FieldsDescription
typepgsql
portConfigurable
methodNot supported
URLNot supported
matchesdefault
oco

This probe attempts to establish a TCP connection on port 79 of your server and checks that the response starts with a "2" (success). This probe has no specific configuration options.

FieldsDescription
typeoco
portNot configurable
methodNot supported
URLNot supported
matchesdefault

From the OVHcloud Control Panel

You can configure probes when you add or modify a server farm, in advanced settings.

Advanced farm settings

You will then have access to the configuration for the probe type.

Probe settings

If the probe type you have selected allows it, you can configure advanced settings that are specific to that probe.

Advanced probe settings

A new configuration window will appear, with the probe's settings.

Advanced probe settings

Go further

Join our community of users.

¿Le ha resultado útil esta página?